    Add a new rad to Combi system.

    hey folks,

    I have a combi boiler and want to add a Towel radiator to the system.

    the radiators are on the wall as follows:
    .*................*
    **************
    .*................*
    **************
    .*Towel rad....*
    **************
    .*................*
    (a)................(b)

    .-------------
    |.............|
    |.............|
    |normal rad|
    |.............|
    .-------------
    (c)...........(d)

    Now currently (c) and (d) are connected to the boiler

    But what I want to do, is connect:

    (d) to the boiler
    (c) to (b)
    (a) to the boiler....

    What is the best method to do this without flooding the hoose???

    any help gratefully received Hidden Content
    Last edited by nss1888; 28-09-2007 at 10:48 AM.
    Hidden Content Ahh if only..

    Hidden Content
    Hmmm, Uber Dorky Nerd King... I feel like I belong Hidden Content

  2. #2
    Legend stickywicket's Avatar
    Join Date
    Sep 2006
    Posts
    698
    Post Thanks
    Chats
    0
    Rep Power
    18

    Re: Add a new rad to Combi system.

    call a plumber Hidden Content !!! otherwise youll need to turn off the water and drain the system. turn the water off at the mains (stopcock) then test by turning on the water to make sure its off. then youll need to empty your water tank by running the hot water in your bath or similar.

    below is a rough guide that shows a diff method but you get the idea, the way ive mentioned above is how ive seen it done.

    Hidden Content

    Hidden Content
    Last edited by stickywicket; 28-09-2007 at 04:12 PM.

  3. #3
    Member rom10's Avatar
    Join Date
    Jan 2008
    Posts
    125
    Post Thanks
    Chats
    0
    Rep Power
    17

    Re: Add a new rad to Combi system.

    all you need to do is turn off the thormostat and the shut of at the other side drain rad down take off put new rad on the same way as you took off you will get a little water on floor

  4. #4
    Member TEEPEE's Avatar
    Join Date
    Aug 2006
    Location
    bradford, west yorkshire
    Age
    61
    Posts
    58
    Post Thanks
    Chats
    0
    Rep Power
    18

    Re: Add a new rad to Combi system.

    right. you dont need to turn the water off as it is a sealed system on a comi so you have the same water in the system at all times. just turn off the feed valves just under the boiler for the central heating. then drain the system vis he drain valve. (usually loctaed on a downstais rad. then take off te old rad and replace with the towel rail. then refil the system via the filler tap (normally just below the boiler.) bleed all the system( you know how to do this?) then off you go mate. hope this helps. if you want full details email me. i am a gas engineeer

  5. #5
    Member graham1888's Avatar
    Join Date
    Aug 2007
    Location
    Glesga
    Posts
    31
    Post Thanks
    Chats
    0
    Rep Power
    0

    Re: Add a new rad to Combi system.

    I did it last week. Like the previous posts say, you do not have to drain the system. combi boilers have no water tank. I bought some 15mm chrome pipe , a couple of nice shiny valves and a couple of chrome angled compression joins. I had to do it this way as the pipes were coming from the floor and it was tiled. So i did not fancy lifting the tiles. Make sure you dont over-tighten the valves or compression joins or you will bend the olives inside(i found out the hard way) and you will need to get new olives. I am not a plummer but was well impressed with the results. Give it a go. If all else fails, phone mario.

    Cheers.

  6. #6
    Member Not_much_cop's Avatar
    Join Date
    Aug 2006
    Location
    Essex
    Posts
    230
    Post Thanks
    Chats
    0
    Rep Power
    18

    Re: Add a new rad to Combi system.

    You shouldn't really join rads in series, they should be paralleled.
    So from your drawing above (C) and (D) should remain connected to the boiler and you should "T" off of (C) & (D) to (A) & (B) respectfully.

    This is especially true if the rad has thermostats fitted, because if it gets hot enough then the rad will turn off, thus turning your towel rail off too.

    Just my 2 pence worth.

    NMC
    Hidden Content Reality is a state of mind caused by the lack of alcohol Hidden Content

    Hidden Content

Similar Threads

  1. Blade 8000 S2/T2 combi
    By shaft56 in forum Blade BM7000s HD Downloads
    Replies: 1
    Last Post: 09-12-2015, 10:43 PM
  2. Gas combi boiler heating question, help.
    By BraveHeart in forum Plumbing and heating
    Replies: 6
    Last Post: 11-03-2009, 10:58 PM
  3. Combi/Condensing Boiler
    By jahhus in forum Plumbing and heating
    Replies: 4
    Last Post: 12-03-2007, 10:30 PM
  4. Shower to suit a Combi Boiler
    By snakehips in forum Plumbing and heating
    Replies: 3
    Last Post: 16-02-2007, 09:16 PM
  5. Combi boiler
    By fondiler in forum Plumbing and heating
    Replies: 11
    Last Post: 28-12-2006, 12:26 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •