    3 Gang 2 Way 10 Amp light Switch

    i brought one of these from b & q and i kinda dnt no how to wire it. could sum1 help me as there as soo many places i could put the wires in and i dnt want to blow the house up.

  2. #2
    Member andywebmail's Avatar
    Join Date
    Sep 2006
    Location
    Essex England
    Posts
    50
    Post Thanks
    Chats
    0
    Rep Power
    18

    Re: 3 Gang 2 Way 10 Amp light Switch

    Is this a direct replacement for an existing one?
    if so you can treat each switch as an individual like this -
    IMPORTANT - TURN OFF THE POWER AT THE DISTRIBUTION BOARD
    Write down or mark with small labels the current positions of the wires on your old switch so you can replace them if you get it wrong.
    Each switch will be in a triangular configuration at the back, having one terminal marked com and two at the other end marked L1 & L2. You must go by this as just using wire positions will not work, some switch manufacturers put their switches the "wrong way up" or alternate their positions to fit them in.
    Transfer the wires from your old switch to the new one using the labeling and com, L1 & L2 positions you noted earlier.
    Never work live
    Hope this helps you.

  3. #3
    Member
    Join Date
    Aug 2006
    Location
    essex
    Posts
    91
    Post Thanks
    Chats
    0
    Rep Power
    18

    Re: 3 Gang 2 Way 10 Amp light Switch

    they where not previously connected to a switch how do i no which wire connects to which terminal?

  4. #4
    Member
    Join Date
    Nov 2006
    Posts
    19
    Post Thanks
    Chats
    0
    Rep Power
    0

    Re: 3 Gang 2 Way 10 Amp light Switch

    tell me how meny cable and what color are they so i can help you

  5. #5
    Member andywebmail's Avatar
    Join Date
    Sep 2006
    Location
    Essex England
    Posts
    50
    Post Thanks
    Chats
    0
    Rep Power
    18

    Re: 3 Gang 2 Way 10 Amp light Switch

    The switches shown are of the 'change-over' type you describe. These have three terminals, a common terminal and one for each of the switch positions L1 & L2.
    The circuit is shown below, the live feed is fed through both switches to the light and the switches are cross connected so that when a switch is operated, the state of the light is changed. As before, this is the diagram for one two way switch set up. Just repeat for the other two.
    NEVER WORK LIVE
    Hidden Content

  6. #6
    Member
    Join Date
    Aug 2006
    Location
    essex
    Posts
    91
    Post Thanks
    Chats
    0
    Rep Power
    18

    Re: 3 Gang 2 Way 10 Amp light Switch

    if it helps i have 1 main wire that is giving the electric and i have 3 other wires that need the electric.

  7. #7
    Member
    Join Date
    Sep 2006
    Posts
    10
    Post Thanks
    Chats
    0
    Rep Power
    0

    Re: 3 Gang 2 Way 10 Amp light Switch

    do you have other switches controlling the lights?
    where are the cables that need the electric going too?
    Not enough info to tell you any more for now.
    The drawing above is for 1 to 2 way conversion good chance its not what your after.
    Last edited by sandy; 10-11-2006 at 07:44 PM.

  8. #8
    Member andywebmail's Avatar
    Join Date
    Sep 2006
    Location
    Essex England
    Posts
    50
    Post Thanks
    Chats
    0
    Rep Power
    18

    Re: 3 Gang 2 Way 10 Amp light Switch

    1. prepare 2 short pieces of wire to bridge the 3 terminals marked "com" (one on each switch)
    2. connect the live wire to one of these com connections. (this will supply power to all 3 switches)
    3. connect the three live wires that go to the lamps to the L1 connection on EACH switch. (one wire per switch)
    4. Join all the neutrals together in a single " Chockblock " connector.
    REMEMBER POWER OFF WHILE WIRING
    Last edited by andywebmail; 11-11-2006 at 08:11 PM.

  9. #9
    Member
    Join Date
    Aug 2006
    Location
    essex
    Posts
    91
    Post Thanks
    Chats
    0
    Rep Power
    18

    Re: 3 Gang 2 Way 10 Amp light Switch

    so i put the 2 bridges in the 3 coms so they are conneted up then i attach the live wire coming from the mains the the com. then what do i do with the neautral coming from the mains? and what do i do with the 3 sets of lives and neutrals for the 3 lights?

  10. #10
    Member
    Join Date
    Aug 2006
    Location
    essex
    Posts
    91
    Post Thanks
    Chats
    0
    Rep Power
    18

    Re: 3 Gang 2 Way 10 Amp light Switch

    can any one help me please

  11. #11
    Member andywebmail's Avatar
    Join Date
    Sep 2006
    Location
    Essex England
    Posts
    50
    Post Thanks
    Chats
    0
    Rep Power
    18

    Re: 3 Gang 2 Way 10 Amp light Switch

    Wire the switches as advised in my last post, your reading of it was correct.
    Then get a single piece of " chockblock " type connector and join ALL the neutrals together.
    That should be it.

  12. #12
    Member
    Join Date
    Aug 2006
    Location
    essex
    Posts
    91
    Post Thanks
    Chats
    0
    Rep Power
    18

    Re: 3 Gang 2 Way 10 Amp light Switch

    so i put the three lives in l1 and the 3 neutrals joined up together

  13. #13
    Member andywebmail's Avatar
    Join Date
    Sep 2006
    Location
    Essex England
    Posts
    50
    Post Thanks
    Chats
    0
    Rep Power
    18

    Re: 3 Gang 2 Way 10 Amp light Switch

    One live to the lamps in one L1 in EACH switch.
    Join ALL neutrals together in a seperate chockblock.
    Do the bridging bit first & include your live supply wire in with the bridge on the coms.
    Ive edited the earlier instructions to make it more suitable to what you are doing.
    “When you help someone up the hill, you are closer to the top yourself.”Hidden Content

  14. #14
    Member andywebmail's Avatar
    Join Date
    Sep 2006
    Location
    Essex England
    Posts
    50
    Post Thanks
    Chats
    0
    Rep Power
    18

    Re: 3 Gang 2 Way 10 Amp light Switch

    1. prepare 2 short pieces of wire to bridge the 3 terminals marked "com" (one on each switch)
    2. connect the live wire to one of these com connections. (this will supply power to all 3 switches)
    3. connect the three live wires that go to the lamps seperatley to the L1 connection on EACH switch. (one wire per switch)
    4. Join all the neutrals together in a single " Chockblock " connector.
    REMEMBER POWER OFF WHILE WIRING
    “When you help someone up the hill, you are closer to the top yourself.”Hidden Content

  15. #15
    Member
    Join Date
    Aug 2006
    Location
    essex
    Posts
    91
    Post Thanks
    Chats
    0
    Rep Power
    18

    Re: 3 Gang 2 Way 10 Amp light Switch

    what is a " Chockblock "?

  16. #16
    Member
    Join Date
    Jun 2006
    Location
    Stoke on Trent
    Age
    67
    Posts
    7
    Post Thanks
    Chats
    0
    Rep Power
    0

    Re: 3 Gang 2 Way 10 Amp light Switch

    Hidden Content Originally Posted by THE DADDY Hidden Content
    what is a " Chockblock "?
    A chockblock is a terminal connector strip which is dark brown and large enough to take 3 wires

  17. #17
    Member andywebmail's Avatar
    Join Date
    Sep 2006
    Location
    Essex England
    Posts
    50
    Post Thanks
    Chats
    0
    Rep Power
    18

    Re: 3 Gang 2 Way 10 Amp light Switch

    Hidden Content
    This is a Chockblock or terminal connector strip.
    Available at all electrical outlets. Very cheap.
    You will only need one terminal off the end of a strip which you just cut off.
    Put all the neutral wires in one of these to join them ALL.
    “When you help someone up the hill, you are closer to the top yourself.”Hidden Content

  18. #18
    Big Bad Boss Gazer's Avatar
    Join Date
    May 2006
    Location
    Marsss
    Posts
    3,673
    Post Thanks
    Chats
    8
    Rep Power
    10

    Smile Re: 3 Gang 2 Way 10 Amp light Switch

    lmao only just seen this Hidden Content

    @THE DADDY
    well did you end up like andywebmail or did it work ?? Hidden Content

    and i got to say i could not of put it any better andy nice one m8 Hidden Content

    Regards Gazer
    Hidden Content
    Viewing Pay TV without a valid subscription is illegal!
    All the files available on this forum are kept for experimental and educational purpose only!

    Hidden Content

  19. #19
    Member andywebmail's Avatar
    Join Date
    Sep 2006
    Location
    Essex England
    Posts
    50
    Post Thanks
    Chats
    0
    Rep Power
    18

    Re: 3 Gang 2 Way 10 Amp light Switch

    Thanks Gazer, I work as an Electrical engineer so its no probs to help The Daddy out (and anyone else that posts electrical questions). I joined the forum to find out more about the d b*xs but have found loads of other interesting stuff. Great forum mate.

    All the best.
    “When you help someone up the hill, you are closer to the top yourself.”Hidden Content

  20. #20
    Member
    Join Date
    Aug 2006
    Location
    essex
    Posts
    91
    Post Thanks
    Chats
    0
    Rep Power
    18

    Re: 3 Gang 2 Way 10 Amp light Switch

    done it mate but now face another problem

Similar Threads

  1. light switch wiring
    By digitalman in forum Electrical
    Replies: 0
    Last Post: 05-06-2011, 08:26 PM
  2. hi gang
    By whitetop in forum Who Are You ?
    Replies: 5
    Last Post: 08-11-2010, 03:54 PM
  3. How do I tile around a light switch
    By Jango in forum DIY Discussions
    Replies: 10
    Last Post: 16-03-2008, 12:35 AM
  4. Hi Gang !
    By jayyou in forum Who Are You ?
    Replies: 3
    Last Post: 03-07-2006, 07:10 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •